F6High-pressure control (in cooling mode)
Name in the manufacturer's documentation (user manual): High-pressure control (in cooling mode)
[1]
In plain words (editorial)
High-pressure control in cooling mode: the outdoor heat exchanger is too hot. The service manual's first step is to clean the outdoor heat exchanger; it also lists closed stop valves, the thermistor and the expansion valve.
When to call a service technician: Cleaning the outdoor heat exchanger and further checks are best left to a service technician.
✎ editorial – written from the cited sources, not a manufacturer statement. Status: draft.
For technicians
Detection conditions (source text)
- Outdoor heat exchanger thermistor measures a too high temperature[2]
Possible causes (source text)
- Dirty outdoor heat exchanger[3]
- Closed stop valve in the refrigerant circuit[4]
- Faulty heat exchanger thermistor[5]
- Faulty expansion valve[6]
- Faulty main pcb[7]
- Refrigerant overcharge[8]
- Non‑condensables and/or humidity in the refrigerant circuit[9]
- Clogged refrigerant circuit[10]
- Faulty outdoor unit fan motor[11]
Steps given by the manufacturer (source text)
- Clean the outdoor heat exchanger[12]
- Check that all stop valves of the refrigerant circuit are open[13]
- Perform a check of the heat exchanger thermistor[14]
- Perform a check of the expansion valve[15]
- Perform a check of the main pcb[16]
- Check if the refrigerant circuit is correctly charged[17]
- Check for the presence of non‑condensables and/or humidity in the refrigerant circuit[18]
- Check if the refrigerant circuit is clogged[19]
- Perform a check of the outdoor unit fan motor[20]
⚠ Work on refrigerant circuits, mains electricity and PV DC wiring is for qualified technicians only.
The Polish page has more detail (plain-language explanation, safe checks, guides): Read in Polish →
Sources
Every statement has a footnote to the document and PDF page. “Quote verified” means the quote was found automatically in the text of that page.
⚠ Some information comes from unofficial sources (copies shared by users, transcriptions, forums). They are marked below. Check them against the manufacturer's documentation before working on the device.
- [1] Daikin – User reference guide FTXF20~42E5V1B + ATXF20~42E5V1B, 4D526466-14K (2022.09) (4DEN526466-14K) , p. 37 official manufacturer document checked manually
High-pressure control (in cooling mode)
- [2] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
outdoor heat exchanger thermistor measures a too high temperature.
- [3] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
dirty outdoor heat exchanger.
- [4] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
closed stop valve in the refrigerant circuit.
- [5] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
faulty heat exchanger thermistor.
- [6] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
faulty expansion valve.
- [7] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
faulty main pcb.
- [8] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
refrigerant overcharge.
- [9] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
non‑condensables and/or humidity in the refrigerant circuit.
- [10] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
clogged refrigerant circuit.
- [11] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
faulty outdoor unit fan motor.
- [12] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
clean the outdoor heat exchanger.
- [13] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
check that all stop valves of the refrigerant circuit are open.
- [14] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
perform a check of the heat exchanger thermistor.
- [15] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
perform a check of the expansion valve.
- [16] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
perform a check of the main pcb.
- [17] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
check if the refrigerant circuit is correctly charged.
- [18] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
check for the presence of non‑condensables and/or humidity in the refrigerant circuit.
- [19] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
check if the refrigerant circuit is clogged.
- [20] Daikin – Service manual Split Sensira R32 FTXF20~71A + FTXF20~25B + FTXF20~42C (+ ATXF/RXF/ARXF), ESIE18-12E – 2021.02 – text capture of pp. 2–36 from easymanua.ls (ESIE18-12E) , p. 17 ⚠ unofficial source quote verified
perform a check of the outdoor unit fan motor.