Panasonic · Heat pumps · Panasonic Aquarea Bi-bloc (split), generation H
F12Pressure switch activate
Name in the manufacturer's documentation (service manual): Pressure switch activate
[1]
In plain words (editorial)
The refrigerant pressure rose too high and the high-pressure safety switch tripped several times. The service manual's causes include poor heat transfer (dirty heat exchanger, blocked air flow) and too little water flow.
When to call a service technician: If it repeats, call the installer; refrigerant work needs an F-gas technician.
✎ editorial – written from the cited sources, not a manufacturer statement. Status: draft.
For technicians
Detection conditions (source text)
Possible causes (source text)
- Dust accumulation on the outdoor unit heat exchanger.[4]
- Air short circuit at outdoor unit.[5]
- Faulty water pump.[6]
- Insufficient water flow rate in system.[7]
- Water leak in system.[8]
- 2/3 way valve closed.[9]
- Clogged expansion valve or strainer.[10]
- Excessive refrigerant.[11]
- Faulty outdoor high pressure sensor and switch.[12]
- Faulty outdoor unit PCB.[13]
⚠ Work on refrigerant circuits, mains electricity and PV DC wiring is for qualified technicians only.
The Polish page has more detail (plain-language explanation, safe checks, guides): Read in Polish →
Sources
Every statement has a footnote to the document and PDF page. “Quote verified” means the quote was found automatically in the text of that page.
- [1] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 153 manufacturer document – copy from a distributor quote verified
F12 Pressure switch activate
- [2] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
During operation of cooling and heating, when pressure 4.5 MPa and above is detected by outdoor high pressure switch.
- [3] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Continue 4 times in 20 minutes.
- [4] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Dust accumulation on the outdoor unit heat exchanger.
- [5] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Air short circuit at outdoor unit.
- [6] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Faulty water pump.
- [7] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Insufficient water flow rate in system.
- [8] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Water leak in system.
- [9] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
2/3 way valve closed.
- [10] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Clogged expansion valve or strainer.
- [11] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Excessive refrigerant.
- [12] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Faulty outdoor high pressure sensor and switch.
- [13] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 181 manufacturer document – copy from a distributor quote verified
Faulty outdoor unit PCB.