Panasonic · Heat pumps · Panasonic Aquarea Bi-bloc (split), generation H
F95Cooling high pressure overload protection
Name in the manufacturer's documentation (service manual): Cooling high pressure overload protection
[1]
In plain words (editorial)
In cooling mode the refrigerant pressure is too high and the overload protection stopped the unit. The causes listed by the service manual for this unit are shown in the technical section below.
When to call a service technician: If the code repeats, call a service technician.
✎ editorial – written from the cited sources, not a manufacturer statement. Status: draft.
For technicians
Detection conditions (source text)
- During operation of cooling, when pressure 4.0 MPa and above is detected by outdoor high pressure sensor.[2]
Possible causes (source text)
⚠ Work on refrigerant circuits, mains electricity and PV DC wiring is for qualified technicians only.
The Polish page has more detail (plain-language explanation, safe checks, guides): Read in Polish →
Sources
Every statement has a footnote to the document and PDF page. “Quote verified” means the quote was found automatically in the text of that page.
- [1] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 154 manufacturer document – copy from a distributor quote verified
F95 Cooling high pressure overload protection
- [2] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
During operation of cooling, when pressure 4.0 MPa and above is detected by outdoor high pressure sensor.
- [3] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Dust accumulation in the outdoor unit heat exchanger.
- [4] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Air short circuit at outdoor unit.
- [5] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
2 way valve closed.
- [6] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Faulty outdoor unit fan motor.
- [7] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Clogged expansion valve or strainer.
- [8] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Excessive refrigerant.
- [9] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Faulty outdoor high pressure sensor.
- [10] Service Manual – WH-SDC03/05/07/09H3E5-1 + WH-UD03/05/07/09HE5-1 (PAPAMY1703036CE) , p. 202 manufacturer document – copy from a distributor quote verified
Faulty outdoor unit PCB (main).